Will there be a significant voltage drop if a 60 FT 8-4 extension cord is used to connect appliances to a 7500W generator?

[Edit]

Answer

no but you cant exceed the wattage of the generator if you are close to that amount you will notice a reduction not nescessarily in voltage but amperage which will have the same affect

Answer

If the generator is 7500 watts, 240 volts, that is approximately 30 amps maximum load. According to one online calculator for voltage drop, your AWG 8 wire run would have only a 3 percent drop over 95 feet or so, or 120 feet if you're only using 25 amps.

Ref: www.elec-toolbox.com/calculators/voltdrop.htm

Improve Answer Discuss the question "Will there be a significant voltage drop if a 60 FT 8-4 extension cord is used to connect appliances to a 7500W generator?" Watch Question

First answer by ID0000000000. Last edit by Wutzyerproblem. Contributor trust: 584 [recommend contributor]. Question popularity: 138 [recommend question]

Research your answer:

Answers.com > Wiki Answers > Categories > Home and Garden > Home Improvement > Home Electricity > Will there be a significant voltage drop if a 60 FT 8-4 extension cord is used to connect appliances to a 7500W generator?

Our contributors said this page should be displayed for the questions below. (Where do these come from)
If any of these are not a genuine rephrasing of the question, please help out and edit these alternates.
Will there be a significant voltage drop if a 60 FT 8-4 extension cord is used to connect appliances to a 7500 watt generator?  Will voltage drop exceed 5 percent using a 60ft AWG 8-4 extension on a 7500 Watt generator?